Earth Fault Relay Settings for 11kv Distribution Feeders

In the power distribution company where I work, the earth fault relays are usually set to 20% of the nominal feeder current. I have also seen online sources that specify between 10% and 20% for earth fault settings.

I am aware that even in an unbalanced load situation, there is a very negligible ground fault current. So I wonder why go as high as 10%? Why not 2% or even 1%?
 
F

Freakboynv2000

This is to avoid nuisance tripping. You don't want your settings so tight that any small transient event will cause an outage.
 
Thanks for your reply.

>This is to avoid nuisance tripping. You don't want your
>settings so tight that any small transient event will cause
>an outage.

Will transients typically or even sometimes result in earth fault current flowing, when there is no actual earth fault present? I understand that during restoration, CT saturation may result in a phantom earth fault.
 