ELLIOT COMPRESSOR ERROR 215

Hi,
we have elliot compressor running on XYCOM control system, one day all of sudden it started showing error 215,
When enquired about it, vendor suggests its either the problem with CPU, Memory board or EEPROM.
We have changed the memory card and CPU as well, but now program is stuck at PAP Phase 2 Software is starting, please wait.
 
Hi

Did you either run the diagnostic test sequence...as per OEM recommandation when changing CPU/MEMORY CARD...

Are the settings correct for CMOS and other boards jumpers ok for CPU

Is system operating under MS DOS/BIOS if yes check proper setting :
Jumper Settings

The following table lists the functions of all the jumpers on the 4117T. The following

sections describe how to set jumpers on the ICPMB-7570 board.

Label

JP2

CMOS State Setting



JP4 CF Card Setting

JP5 LCD Voltage Setting

JP6 COM3 Mode RS-232 or RS-485 Setting
JP2: Clear CMOS Setup

If the CPU Card fails to boot due to improper BIOS settings, use this jumper to clear

the CMOS data and reset the system BIOS information. To do this, use the jumper cap

to close pins 2 and 3 for a few seconds then reinstall the jumper clip back to pins 1 and

2.

If the "CMOS Settings Wrong" message displays during the boot up process, you may

then try to correct the fault by pressing the F1 to enter the CMOS Setup menu. You

may then do one of the following:

Enter the correct CMOS setting

Load Optimal Defaults

Load Failsafe Defaults.

Caution

Table 3-1. Jumper Functions

CMOS State Setting

CF Card Setting

LCD Voltage Setting

COM3 Mode RS-232 or RS-485 Setting

17

Chapter 3 – ICPMB-7570 CPU Board & BIOS Setup

Function

...PLZ Clarify type /model of Touch panel interface...I guess that is PROFACE but we need serial number as they are different models available...

Thanks for your clarifications..

James
 
Hi,
Thanks for responding.
No we have not run diagnostic test, we have changed the CPU card on consultation with vendor,
Earlier we had a Greenspring CPU card, but the spare one is XYCOM CPU card.
Memory Card : XVME 505/2
On applying new CPU card and New memory card it shows Phase 2 PAP software is starting, Please wait, and it gets stuck to it.
If I apply old CPU card and new memory card it shows
BRAM:080000 FP overflow; PC=890e24,
SP=00cbe8,(SP)=880b60.

On applying old CPU card and old memory card it simply shows error 215
Is there any change in jumper setting on migrating from Greenspring card to Xycom card.
 
Hi,
Thanks for responding.
No we have not run diagnostic test, we have changed the CPU card on consultation with vendor,
Earlier we had a Greenspring CPU card, but the spare one is XYCOM CPU card.
Memory Card : XVME 505/2
On applying new CPU card and New memory card it shows Phase 2 PAP software is starting, Please wait, and it gets stuck to it.
If I apply old CPU card and new memory card it shows
BRAM:080000 FP overflow; PC=890e24,
SP=00cbe8,(SP)=880b60.

On applying old CPU card and old memory card it simply shows error 215
Is there any change in jumper setting on migrating from Greenspring card to Xycom card.
Hi,

Thanks for your inputs...

Still remain the Type /model/serial number of the device it self unknow , can you clarify ...


Also it can be possible that you need to upload drivers or at least check if drivers are updated...

Will have a closer view on this thread , see how i can support ...

James
 
Top