error S7

  • Thread starter gino mettepenningen
  • Start date
G

Thread Starter

gino mettepenningen

i have a error mention, it's loud FUNCTION NOT IMPLEMENTEND (33:496), it's happend while i download fb's and fc's to the contoller, what does it means?
 
D

Daniel Chartier

Hello;
I've seen this message when trying to download a function block that is not allowed on the particular CPU in the project. For example, integrated functions (high-speed counter or pulse output) on anything but a S7-312IFM or S7-314IFM; or when we used too large a FB/FC/DB number; a S7314, for example, would refuse any reference to a FB257 (it allows only up to FB255). Check the programming reference for your CPU, or the online help.

Hope this helps,
Daniel Chartier
 
D

Donald Pittendrigh

Hi All

This comes from trying to download SFB's, SFC's or standard OB's which are not part of that PLC's subset, into the PLC. It usually occurs as a result of copying the above blocks, (all of them) from the standard library instead of selecting
only the ones you require. If you keep a list of the blocks referenced in the error messages and delete them off your backup, the problem should go away.

Regards
Donald Pittendrigh
 