Explosion Proof Process Controller

P

Thread Starter

PP Muthu

Hi
For an on-going project we are looking for
Electronic Field Mounted Controllers (30 Nos)

- Output: 4-20 mA or 3-15 PSI
- Ex-proof/non-incendive, suitable for Class 1, Div 2 Gr B,C,D.

Please inform me if anyone knows any manufacturers/supplier.

Thanks & Best Regards
PP Muthu
Rezayat, Kuwait
 
D

david mertens

A project I was involved in some 5 years ago had field controllers from foxboro and from endress+hauser, however they were fully pneumatical so we used I/P and P/I converters (Eexia) from samson to convert the measurements to pneumatical (0.2 - 1 bar) and the outputs to electrical (4 - 20 mA).
 
Allen Bradley has Flex Ex I/O suitable for Class1 Div1 installation. They have discrete I/O as well as analog input and output modules. You can use a Controlnet Ex adaptor module for interfacing between the Flex Ex modules and the PLC.
 