Final year project using Honeywell DCS

A

Thread Starter

AbhilashKondodi

i am working on my final year project, "Automation of a batch process using Honeywell DCS HC900 C30".

I have almost completed with Functional Block Diagram part done in Hybrid control designer software.

I want to know if i could use some SCADA software? If yes, Which?
Is there any inbuilt Software for DCS or related software for Honeywell DCS which would perform Process data gathering function and representation in a neat way?

Please Help!

Regards,
Abhilash
[email protected]
Final Year Instrumentation
 
Current firmware 4.4 (or higher) HC900 controllers can use flash memory in the controller's CPU for tag value data storage.

The best description (with great graphics and illustrations) is the 'HC900 CPU data storage and retrieval app note', available here::
http://tinyurl.com/m6cpqt4
preview: http://preview.tinyurl.com/m6cpqt4

Honeywell's Control Station CS-900 HMI panel can also log data to its flash memory, and has multiple screen trending functionality built in.

For DCS/SCADA/HMI connectivity, the HC-900 is a native Modbus slave and master.

One can choose the factory assigned register map (when the HC is a slave) or create a custom map for specific tags. Hence any HMI panel, HMI software or OPC server with Modbus RTU or Modbus/TCP functionality can easily communicate with an HC-900 controller.

A slide review of HC-900's Modbus functionality is here:
http://www.scribd.com/doc/214768348/Honeywell-HC900-Modbus-RTU-TCP-Overview
http://tinyurl.com/m2j8eyq
http://preview.tinyurl.com/m2j8eyq

A slide review of HC-900 fixed or custom Modbus mapping is here:
http://www.scribd.com/doc/214769277/Honeywell-HC900-Modbus-Map-Fixed-or-Custom
http://tinyurl.com/n3lv4se
http://preview.tinyurl.com/n3lv4se
 