O
hello guys,
while starting on diesel fuel, a strange phenomena happens which is from the moment the L3FIRE is true,and the machine fires, during the 60 sec wrm-up, there is very high fluctuation in FAL from 36% to -7%, then followed by a flactuation in diesel flow A60FQI from 0.2 gpm to 11 gpm, this caused the flame to come on and go off several times, the FSR1 was fixed at 19.5%, and the FQROUT was 3.6%, and the FQL1 was flactuating between 0.6% to 7%, (the TCQA requlator current-gain is 1.55 & current-bias is 2.71).
these parameters were flactuating until the speed reached about 46%, at this speed, all became much smoother, and all flactuations normalized,and the machine proceeded to accelerate, until the speed reached 90%, at this speed, very huge increase in diesel fuel took place, which went up from 14 gpm to 37 gpm, followed by very sharp flactuation in FAL, FQROUT, and the FSR1, it went on until a change-over to gas command took place. a previous change from Gas to Diesel on the same machine was carried over before, but the machine tripped on Turbine Underspeed trip, which caused by very high diesel flow which might cuz the flame to be less tensive, so i really wish if i get any feedback analyzing the phenomena.
i tried to post a sample of the view2 here, but it didn't work, so if any of you guys interested, i can send you the text document of the view2 to better analyze this problem.
any feedback will be highly appreciated.
thank you in advance.
Omar
[email protected]
Omar
[email protected]