We have two Frame -5 GE gas turbines of 18 MW each. Last week both turbines were on normal operation. Total load was 26 MW and each turbine was on 13 MW.
TG_1 (Mark-II Control) was on ISO mode while the TG_2 (Mark-V control) was on droop mode.
A heavy flash (short circuit) took place in one of the sub stations. Most probably under voltage relay 27 was actuated for a short time, which causes the load shed by the load shedding system.
Then it was observed that the breaker of TG_1 open and load on TG_2 was 5 MW. As the TG_2 was on droop and its frequency was raised to 53.5 Hz.
Now the question is:
Why did the TG-2 go to 53.5 Hz (5446 RPM) while the droop is 4%? And in CSP it is written set point high speed stop 107% and set point low speed stop 95% TNKR3 & TNKR4 respectively? While turbine was in normal operation its signal was on 13 MW but on 5 MW how its signal was raised up to about 107%.