Our State of the Art Frame-5 GE Gas Turbine tripped on high explosivity on sensing 10% of LEL of value on 2oo3 security installed at the outlet of the compartment exhaust duct. The compartment is a forced draft one with one fan in operation. Prior to tripping there was a spike of explosivity that came 4 hrs back and touched alarm value of 6% of LEL but came down in a minute or so to the normal value (set at 3 % of LEL as a 0 value). One spike also came 4 to 5 hours before the second last spike and normalized. Unfortunately we don't have a trend available and all the data is based on observations by operator. One thing that has been noted that plant start-up was in progress and there is a CO2 gas vent nearby that contains 1 to 2% H2. We are suspecting that some of the gas entered into the filter house and channeled into the Gas Turbine compartment via forced draft fan and caused the 3 sensors of explosivity to read above 10% LEL and tripped the turbine. Although as per own knowledge the explosivity meters are based on LEL of Methane gas, we are suspecting that they are also sensitive to H2. Has anybody experienced such spikes of explosivity which caused all the three sensors to reach trip value? It is interesting to note that sensors became normal after gas turbine tripping and did not read high values after gas turbine was started again and given upto 12 MW load. However this time the process plant (NH3 and Urea Units) was running normal with no start-up in progress. This ruled out the possibility that there was any leakage inside the compartment. We are now suspecting some outside source or malfunction of sensors. Even the chances of malfunction of sensors may be remote as all three sensors reached alarm values ten second before tripping before gas turbine tripped on reading two sensors at trip values. Please comment.