GE Fanuc PLC Alarm

D

Thread Starter

DEWA

we have GE fanuc PLC in Gas plant and we have an alarm ACTION HANDLER FAULT. we don't know what does it mean?

all the data we have about this alarm is"
Cstomer Tag: FL52
Modbus Address 1831
Setting Fault=1
 
One will need MUCH MORE information to help you with this.
You may be better and quicker served by contacting the original developer and/or reading the documentation for your system.
At least check the description of Tag: FL52.
 
M

Mohammad Elkhaiat

my friend,

this all the informations i have about this alarm, and i don't find any thing in manuals to help me. i don't know whether it is a PLC fault or another issue.
 
> this all the informations i have about this alarm, and i don't find any thing
> in manuals to help me. i don't know whether it is a PLC fault or another issue.

It is not a standard or recognizable GE IP or GE Fanuc 90-30 PLC fault.
Or any other GE Fanuc PLC fault that I can recognize. I suggest that you contact the original developers for assistance.

HTH
 