Dear Sir,
We are operating GE frame 7FA DLN 2.6 gas turbines in Kingdom Of saudi Arabia,
We have two units of GE frame 7FA DLN 2.6
we did Unit#01 Major Inspection in OCT-12 and UNIT#02 MI in NOV-12
After major inspection initially both machine delivering the more of less same output (165 MW)
But since JAN-13 the Unit#01 performance was degrading. we did Unit#01 water wash in MARCH-13. after water wash Unit#01 output crossed Unit#02 (almost 5 to 6 MW higher than unit#02)
but what we observed that unit#01 output again degrading just after 3 days of offline water wash.
After water wash of unit#01, the exhaust temperature was found only 584 degc and TTRF1# 1300 degc. we traced the past trend and found that exhaust temp remained around 615 degc and the reference TTRF1# 1317 degc
there was an alarm just after the offline water wash that AFPAP difference high between the units
AFPAP (atmospheric pressure) reading was found lower than unit#02 after Unit#01 off line water wash
1. GT#01, Exhaust thermocouple TTDX#13 reading# 548 degc and the TTXSP1# 70 degc. we may have to parallel TTXD#13 with healthy thermocouple
2. Also “AFPAP difference high between the units” alarm appeared and persisting
GT#01 AFPAP # 27.7 In/In
GT#02 AFPAP# 29.77 in/in
If difference goes above 0.5 in/in, high difference between units alarm will appear
3. Exhaust temperature (TTXM) came down from 624 degc to 600 degc
4. CPD increased from 13.55 bar to 14.17 bar
5. CTD decreased from 397.35 degc to 395.74 degc
6. Unit#01 MW increased from 150 MW to 157 MW
We did Unit#01 offline water wash on 3rd march-13, and on 05th march-13 we observed unit#01 MW was 3 MW lower than Unit#02
GE recommended to do calibration of unit#01 AFPAP transmitter. transmitter was calibrated and the reading back to normal same as GT#02
after AFPAP calibration Unit#01 MW crossed 4 MW higher than Unit#02
Following parameters were increased after GT#01 AFPAP calibration
1. TTRF1 increased from 1300 to 1317 degc
2. FSR increased from 70% to 72%
3. MW increased from 155 MW to 161 MW
Can you please share your expert knowledge regarding above subject?
Why the Reference temperature gone down after the offline water wash?
what are the inputs to calculate the TTRF1?
Your help in this regard is much appreciated
Thanks
Parag
We are operating GE frame 7FA DLN 2.6 gas turbines in Kingdom Of saudi Arabia,
We have two units of GE frame 7FA DLN 2.6
we did Unit#01 Major Inspection in OCT-12 and UNIT#02 MI in NOV-12
After major inspection initially both machine delivering the more of less same output (165 MW)
But since JAN-13 the Unit#01 performance was degrading. we did Unit#01 water wash in MARCH-13. after water wash Unit#01 output crossed Unit#02 (almost 5 to 6 MW higher than unit#02)
but what we observed that unit#01 output again degrading just after 3 days of offline water wash.
After water wash of unit#01, the exhaust temperature was found only 584 degc and TTRF1# 1300 degc. we traced the past trend and found that exhaust temp remained around 615 degc and the reference TTRF1# 1317 degc
there was an alarm just after the offline water wash that AFPAP difference high between the units
AFPAP (atmospheric pressure) reading was found lower than unit#02 after Unit#01 off line water wash
1. GT#01, Exhaust thermocouple TTDX#13 reading# 548 degc and the TTXSP1# 70 degc. we may have to parallel TTXD#13 with healthy thermocouple
2. Also “AFPAP difference high between the units” alarm appeared and persisting
GT#01 AFPAP # 27.7 In/In
GT#02 AFPAP# 29.77 in/in
If difference goes above 0.5 in/in, high difference between units alarm will appear
3. Exhaust temperature (TTXM) came down from 624 degc to 600 degc
4. CPD increased from 13.55 bar to 14.17 bar
5. CTD decreased from 397.35 degc to 395.74 degc
6. Unit#01 MW increased from 150 MW to 157 MW
We did Unit#01 offline water wash on 3rd march-13, and on 05th march-13 we observed unit#01 MW was 3 MW lower than Unit#02
GE recommended to do calibration of unit#01 AFPAP transmitter. transmitter was calibrated and the reading back to normal same as GT#02
after AFPAP calibration Unit#01 MW crossed 4 MW higher than Unit#02
Following parameters were increased after GT#01 AFPAP calibration
1. TTRF1 increased from 1300 to 1317 degc
2. FSR increased from 70% to 72%
3. MW increased from 155 MW to 161 MW
Can you please share your expert knowledge regarding above subject?
Why the Reference temperature gone down after the offline water wash?
what are the inputs to calculate the TTRF1?
Your help in this regard is much appreciated
Thanks
Parag