GE Modbus Concentrator

T

Thread Starter

Tharun_CE

facing problem in getting data from microversa trip unit to ge 90-30 plc, by using ge Modbus Concentrator & versamax SET001.

Only getting the fixed register values, not the dynamic & setpoint values,

can any one provide the feedback.

with regards
[email protected]
 
R

Russ Bartels

We need more detail. there is no apparent reason for getting only part of your data unless the other addresses are not supported in the VersaMax or you are trying to make too many connections to the SET001 device, remember this is an Ethernet to Serial and only supports 2 connections at a time.
 
T

tharun_krishna

getting the values from those registers which are 8 bit, but it fails to read the data which are in float datatype from microversa trip units through modbus concentrator to SET001
 
What addresses are you trying to use that do not work?

>getting the values from those registers
>which are 8 bit, but it fails to read
>the data which are in float datatype
>from microversa trip units through
>modbus concentrator to SET001

"Detail in your questions promote details in my answers."
 