V
Our Gas turbine generator got tripped on rotor earth fault while start up after On exciter breaker (Voltage up to 9 KV). Then we have stopped machine and tested rotor to earth and IR value is zero ohm on 100 V megger.
Next we disconnected Generator rotor connection from rotating rectifier wheel and found 3 Mohm and main exciter rotor (diode connections removed at rectifier wheel) value found 1 MOHM. But outlet of rectifier wheel terminal to earth IR valve is only 0.01 MOHM on 100 V megger.
After that we have cleaned all parts of rectifier wheel and IR value doesn't improve.
Pls suggest what we can do for further IR value improvement.