I need some clarification on a problem we are facing in our plant. Ours is a power generation plant. In this plant we have a black start DG, which is used for startup or when power is not available from the grid. The specification of the DG is:
KVA=750
CURRENT=1040
Voltage=415
The make of the Generator is stamford and the engine is a Cummins engine. The out put of the Generator is connected to the main LT busbar for feeding Auxillary loads of the Gas turbine and steam turbine.
It has been observed that when we close this breaker during start ups the breaker trips immediately. Hence the protections have been bypassed and the breaker is closed. We are also not able to get the protection on which the breaker trips.
We are troubleshooting this problem so that the protections can be in line when the DG is started.
The DG has a generator protection relay IM3GV also a reverse power relay MRP11. Also there is a MC61A digital relay.
Can someone suggest how to tackle this problem? Thanks.
KVA=750
CURRENT=1040
Voltage=415
The make of the Generator is stamford and the engine is a Cummins engine. The out put of the Generator is connected to the main LT busbar for feeding Auxillary loads of the Gas turbine and steam turbine.
It has been observed that when we close this breaker during start ups the breaker trips immediately. Hence the protections have been bypassed and the breaker is closed. We are also not able to get the protection on which the breaker trips.
We are troubleshooting this problem so that the protections can be in line when the DG is started.
The DG has a generator protection relay IM3GV also a reverse power relay MRP11. Also there is a MC61A digital relay.
Can someone suggest how to tackle this problem? Thanks.