Getting data to PLC via Circuit Monitor and Modbus

  • Thread starter ART CRUZ_GONZALEZ
  • Start date
A

Thread Starter

ART CRUZ_GONZALEZ

I need to communicate from a Quantum PLC to a Circuit Monitor 4000 via ethernet and from the circuit monitor to other devices via Modbus.

Question is how can I do this in order to get data from the devices attached to the CM 4000 into my PLC?
 
What Ethernet Module do you have installed in the TSX Quantum PLC ? (Part Number: 140NOE771xx)

What Ethernet Adapter do you have installed in the PowerLogic CM4000? (Part Number: EGXxx)

What programming package are you using (Concept Modsoft or ProWORX NxT)?

On the PowerLogic CM4000 there is an additional serial port that can be configured to communiate to a Modbus device. Depending on the Modbus Address of the device you would use the following in your TSX Quantum application.

192.168.0.1 Index 1 --- CM4000 Data
192.168.0.1 Index 2 --- Modbus Device 2
192.168.0.1 Index 3 --- Modbus Device 3

Depending on the Ethernet Moddule installed you will have the following options:

1. I/O Scanner Communication
2. MSTR Communication (Modsoft, ProWORX NxT)
3. IEC Communication Function Blocks (Concept)

Regards
Robert Willis
Square D Company