T
Recently we had one of our gas turbine tripping on exhaust temperature trip though L86TXT was forced, the complete sequence of event is as below. Our's is frame 9 machine with mark v controls.
1.Exh.T/c no. 11 suddenly started giving fluctuating reading so it was decided to check the T/C at field junction box.(we have total 18 nos of T/C)
2.Prior to checking following tags were forced in Mark V
a>L86TXT - Exh.temp. high
b>L86TFB - Exh.T/C open
c>L30SPT- Spread trip
3.Field J.B. was opened and T/C no.11 was disconnected from the terminal strip and was checked for voltage, the reading was found to be fluctuating between 22 mV to 23 mV then resistance of T/C was also checked and it too was found fluctuating between 40 ohms to 50 ohms, as readings were erratic it was decided to make exh. T/C no.17 parallel with T/C.no.11.
4.T/C no.17 & T/C no.11 were made parallel in field JB and both became OK.
5.Prior to closure of JB by mistake the technician connected multimeter to terminals of T/C no.11 to check it's mV and as soon as it was connected machined tripped and on checking alarms on <I> station, high exhaust temperature alarm was first to appear and the reading of TTXM in trip log was also found to be more then 1100 Deg C thus it was concluded that machine had tripped on exhaust temperature high though L86Txt was forced.
6.On checking the multimeter, the selection of same was found to be on continuity checking instead of voltage selection which resulted in high temperature readings at exh. T/C no. 11 & 17 (both being parallel) which resulted in tripping of GT.
Now our query is why GT tripped on high exh. temperature though L86Txt was forced ? Will be a great help if you can share your knowledge/experience of any such incidence that might be in your knowledge or give your views on such an incidence.
1.Exh.T/c no. 11 suddenly started giving fluctuating reading so it was decided to check the T/C at field junction box.(we have total 18 nos of T/C)
2.Prior to checking following tags were forced in Mark V
a>L86TXT - Exh.temp. high
b>L86TFB - Exh.T/C open
c>L30SPT- Spread trip
3.Field J.B. was opened and T/C no.11 was disconnected from the terminal strip and was checked for voltage, the reading was found to be fluctuating between 22 mV to 23 mV then resistance of T/C was also checked and it too was found fluctuating between 40 ohms to 50 ohms, as readings were erratic it was decided to make exh. T/C no.17 parallel with T/C.no.11.
4.T/C no.17 & T/C no.11 were made parallel in field JB and both became OK.
5.Prior to closure of JB by mistake the technician connected multimeter to terminals of T/C no.11 to check it's mV and as soon as it was connected machined tripped and on checking alarms on <I> station, high exhaust temperature alarm was first to appear and the reading of TTXM in trip log was also found to be more then 1100 Deg C thus it was concluded that machine had tripped on exhaust temperature high though L86Txt was forced.
6.On checking the multimeter, the selection of same was found to be on continuity checking instead of voltage selection which resulted in high temperature readings at exh. T/C no. 11 & 17 (both being parallel) which resulted in tripping of GT.
Now our query is why GT tripped on high exh. temperature though L86Txt was forced ? Will be a great help if you can share your knowledge/experience of any such incidence that might be in your knowledge or give your views on such an incidence.