P
CT controller was upgraded from MkV to MkVIe recently. The fuel gas meter is a Rosemount 3095MV multi-variable transmitter. Prior to the MkVIe upgrade I never had any comm issues using a Hart 275, 375 or 475 communicating with this device. While performing a calibration last week, the Hart signal kept dropping out using a 475. I checked connections and performed a Hart diagnosis (23.5 V), but had to continuously cycle power on the 475. Initially I assumed a faulty cable. Changing cables did not resolve the problem. I inserted a 250 Ohm resistor and it helped some, but comm still dropped out but would return much quicker. Has anyone seen this problem? I have never needed to add a resistor before. The Hart 475 in question does operate flawlessly otherwise.