B
I have several heater circuits on our machine, and I'm debating how to hook up the single-phase transformers. I'll need to have to have 2 or 3 transformers to handle the power required of the heaters.
What is the best way to arrange the transformers? I'm debating between two options:
1) I could wire each transformer as a separate single-phase circuit, fusing both legs of the primary and the secondary of each transformer. Thus, the heater circuits (consisting of SSR and heater) would be floating and fused on both legs.
2) I could wire 3 (or 2) transformers in a delta-wye, with a grounded neutral on the secondary, and then I would only require three fuses on the secondary; Each heater circuit (SSR and heater) would then only require a fuse before the SSR, as the other end of the heater is at ground potential.
I'm debating the merits of both options. Option 2 just seems more efficient to me, but option 1 I think is more common. I usually see 240v single-phase circuits floating and fused on both legs, but wouldn't it be possible for a ground fault to trip only 1 fuse and create a hazard? For option 2, is there any potential problem with having a 240v single-phase circuit with one wire being a grounded neutral?
What is the best way to arrange the transformers? I'm debating between two options:
1) I could wire each transformer as a separate single-phase circuit, fusing both legs of the primary and the secondary of each transformer. Thus, the heater circuits (consisting of SSR and heater) would be floating and fused on both legs.
2) I could wire 3 (or 2) transformers in a delta-wye, with a grounded neutral on the secondary, and then I would only require three fuses on the secondary; Each heater circuit (SSR and heater) would then only require a fuse before the SSR, as the other end of the heater is at ground potential.
I'm debating the merits of both options. Option 2 just seems more efficient to me, but option 1 I think is more common. I usually see 240v single-phase circuits floating and fused on both legs, but wouldn't it be possible for a ground fault to trip only 1 fuse and create a hazard? For option 2, is there any potential problem with having a 240v single-phase circuit with one wire being a grounded neutral?