HMI OPC client cannot show Negative values

S

Thread Starter

S.Sivasekar

My Cimplicity HMI with OPC client is connected with Siemens PLC with Siemens OPC server. I can read 0 and positive values, but the negative values are not read on Cimplicity. Why?

Siemens PLC is S7-314 and the OPC Server is Siemens Simatic NET S7/SR-OPC-Server V2.2 Build 1381.
 
S

Steve Myres, PE

Is the display interpreting them as unsigned integer rather than signed integer? If this were happening with a 16-bit integer, for example, -10000 might display as 55,535. Or, is the absolute value correct, as in -10000 shows as 10000? In this case, the HMI would be ignoring the sign bit.
 
D

Donald Pittendrigh

Hi All

Have the same problem with InTouch, the Siemens OPC scout shows the values correctly as negative, I couldn't be bothered and changed all the tags to real numbers, the OPC was so fast anyway and the numbers in the scada didn't suffer from the improved accuracy. Now I only use reals, even in the PLC program.

Donald Pittendrigh
 