How to Connect HoneyWell C300 Server With VB 6.0

  • Thread starter Ranjeet Kumar Bhatia
  • Start date
R

Thread Starter

Ranjeet Kumar Bhatia

Sir,

I want to connect C300 DCS to VB 6.0 to create web page where i can display my boiler temperature and pressure etc and insert data into Oracle Data Base with firewall network security.
 
Hi

C300 EPKS supports ODBC across firewall. Have a firewall in place, configure it to allow only ODBC access from outside and pull the tag values you wish in MS Excel. You will need to install EPKS ODBC driver in the client machine which is outside the firewall, configure the driver to fetch data. This communication across the firewall will use "mngr" a/c credentials of EPKS, so you shall require this a/c in your client machine as well.

From there, it would be rather easy to insert it in Oracle. I don't know if this can done using ODBC where ODBC queries can be used directly to insert the results in oracle.
 