I am getting an "IEC Upload information not restored successfully Error Id: OLI-21735" when uploading from Quantum 140 CPU 434 12 into Concept V2.6.

I can upload the configuration but it fails in the IEC Program sections after uploading them for some time.

The original program was written in 2006 and then modified a few years later when a ProSoft Profibus module was added to the end of the rack. This module does not seem to be in the configuration that I am getting. Below is the config. Any help will be gratefully appreciated

P L C - C o n f i g u r a t i o n

PLC Selection
PLC Type 140 CPU 434 12
Exec Id 883
Memory Size 64K logic
Extended Memory 96K
IEC Runtime Enabled
IEC Usable Memory Size 848

PLC Memory Partition
Coils (0x) 2512 000001-002512
Discrete Inputs (1x) 1008 100001-101008
Input registers (3x) 9999 300001-309999
Holding registers (4x) 9999 400001-409999

ASCII Setup
Total Message 0
Message area size 0
ASCII Ports 0

Configuration Extensions
Data Protection No
Peer Cop Yes
Hot Standby No
Ethernet 1
Profibus DP No

Specials
Battery Coil 001248
Timer Register No
Time Of Day 400700 -400707
Duplicate coils No
First Coil Address -
Watchdog Timeout [ms*10] 30
Online Editing Timeslice [ms] 20

I / O M a p

Remote (Head slot 0)

Drop Type Modules Holdup[ms] Input-Bits Output-Bits
1 Quantum I/O 8 300 160 64

Local Drop
Drop Type: Quantum I/O Drop 1

Slot Module name Input Range Output Range Module description In/Out-Type
1-1 CPS-214-00 DC Summable PS 24V 8A
1-3 DDI-353-00 100001-100032 DC Input 24V 4x8 BIN
1-4 DDI-353-00 100033-100064 DC Input 24V 4x8 BIN
1-5 DDI-353-00 100065-100096 DC Input 24V 4x8 BIN
1-6 DDI-353-00 100097-100128 DC Input 24V 4x8 BIN
1-7 DDI-353-00 100129-100160 DC Input 24V 4x8 BIN
1-8 DDO-353-00 000001-000032 DC Output 24V 4x8 BIN
1-9 DDO-353-00 000033-000064 DC Output 24V 4x8 BIN
 
B
With compiled projects, upload is often a selectable option. Why? To save memory space, and perhaps for security.

Upload is a such a selectable option with Concept. If the project was downloaded without this option selected, then it cannot be uploaded. You can upload the project configuration but not the actual project code.

A problem? Yes if the original code cannot be located. But, this is not a shortcoming of the software. The problem is policy and archiving.

Consider a site with over 400 controllers and numerous support staff. Projects are all set to prohibit upload. Staff gets the current project from the library server, does their troubleshooting and returns the project to the server. This way the current copy is not located on the employees laptop who has just left on vacation and taken the computer with him.

In life, you still have the option of locking your keys in the car and leaving the water running. With Programmable Automation Controllers you also have options.
 