We are equipped with GE 9FA+ turbine which uses MARK VI as control system.
It seems that we have a problem with IGV suddenly not following changes in setpoint.
So we've had first the alarm L86VGA_ALM which comes if for 5 sec command & feedback have a deviation of 7.5%. So what happens is that now IGV has a reference of 83.5% but it remains stuck at 53%. We've checked physical position and it is actually ~50% & movement is not obstructed somehow.
Also input filter DP was checked prior to hydraulic block & it is O.K. We've also stopped the plant & replaced the Moog valve & its filter, stroked it & worked O.K.
After plant startup it worked O.K. for 4 hours & then the same problem occurred.
Can somebody help us out with what else could be checked?
Do you think that if we force reference value for a while less than feedback & then remove force might overpass sticking of the valve?
It seems that we have a problem with IGV suddenly not following changes in setpoint.
So we've had first the alarm L86VGA_ALM which comes if for 5 sec command & feedback have a deviation of 7.5%. So what happens is that now IGV has a reference of 83.5% but it remains stuck at 53%. We've checked physical position and it is actually ~50% & movement is not obstructed somehow.
Also input filter DP was checked prior to hydraulic block & it is O.K. We've also stopped the plant & replaced the Moog valve & its filter, stroked it & worked O.K.
After plant startup it worked O.K. for 4 hours & then the same problem occurred.
Can somebody help us out with what else could be checked?
Do you think that if we force reference value for a while less than feedback & then remove force might overpass sticking of the valve?