Exactly...KHIEBARY,
IF YOU'RE WORKING ON A GE-DESIGN HEAVY DUTY GAS TURBINE WITH DLN COMBUSTORS, YOU SHOULD HAVE EASY ACCESS TO THE OPERATIONS & MAINTENANCE MANUALS AND DOCUMENTATON PROVIDED WITH THE EQUIPMENT. THERE ARE SYSTEM DESCRIPTIONS FOR EACH SYSTEM IN THE MANUAL (SOME ARE BETTER THAN OTHERS) AND THERE IS ALWAYS THE CONTROL SPECIFICATION DOCUMENT FOR THE MARK* AND THE PROGRAMMING IN THE MARK* WHICH CAN BE USED TO DETERMINE/PROVE WHAT'S SUPPOSED TO HAPPEN AND WHEN.
Very elaborate...IBH (Inlet Bleed Heating) is a very poor name for the function it provides. Using IBH allows a GE-design heavy duty gas turbine with DLN-I combustors to transfer into Premix Steady State (the lowest emissions mode) sooner than would otherwise be possible, AND it also allows the unit to remain in Premix Steady State longer when unloading. Without IBH, a GE-design heavy duty gas turbine with DLN-I combustors would transfer into Premix Steady State at about 80% of rated load, and remain in Premix Steady State up to Base Load. Without IBH, when unloading the unit while operating in Premix Steady State the unit will transfer out of Premix Steady state around 80% of rated load, sometimes a little lower. This means the operating range in the lowest emissions mode (Premix Steady State) is between approximately 80-100% of rated load--which for some applications and sites is a very narrow range of operation; some sites need to operate as low as 40-50% of rated load in Premix Steady State (the lowest emissions mode).
So, IBH was "invented." The designers of DLN-I knew that if the axial compressor inlet guide vanes could be closed below the compressor normal minimum operating angle (at rated speed) of 57 DGA (DeGrees Angle) that the turbine could operate in Premix Steady State in a wider range of load. The problem with closing the IGVs below 57 DGA is that the axial compressor can suffer some problems and even damage (sometimes severe) when the IGVs are closed below 57 DGA. The also knew that if a portion of the axial compressor discharge could be extracted before it entered the combustors this would help widen the Premix Steady State operating range. And, further, they knew that if they could decrease the density of air entering the axial compressor even by a little bit the axial compressor would be protected from some of the problems encountered when operating at rated speed with the IGVs closed below 57 DGA.
IBH extracts axial compressor discharge air (a portion of it) and recirculates it a manifold in the axial compressor inlet air duct where it exits the manifold and adds a couple of degrees of heat to the incoming, filtered air entering the axial compressor. This serves to help decrease the density of the air entering the axial compressor which helps to reduce possible damage to the axial compressor when the IGVs are closed below 57 DGA at rated speed. Extracting axial compressor discharge air also reduces the back-pressure on the axial compressor which helps to protect the compressor when the IGVs are closed below 57 DGA when at rated speed. And, recirculating the extracted axial compressor discharge air helps to reduce the energy lost by extracting axial compressor discharge air (which has been compressed by the axial compressor).
When IBH is enabled and active during the start-up of a GE-design heavy duty gas turbine with DLN-I the IGVs will be held to an angle of approximately 42 DGA when the unit reaches rated speed. And, as the unit is loaded the IGVs will be modulated (positioned) to an angle so as not to exceed the maximum allowable exhaust temperature. The net effect of keeping the IGVs closed during starting and initial loading is to reduce the air flow into the combustors, which will allow the unit to transition into Lean-Lean and then Premix Steady State sooner (at lower loads) than would otherwise be possible (that is: without IBH). Most DLN-I combustor-equipped units with IBH enabled and active can transfer into Premix Steady State at loads as low as approximately 40% of rated, and then as the unit continues to be loaded IBH will remain in operation until the IGVs reach approximately 62 DGA, at which time IBH will be deactivated (the IBH control valve will be closed).
Now, as the turbine is unloaded when IBH is enabled (but not yet active!) as the IGVs approached approximately 62 DGA IBH will become active again. As the unit continues to unload, to approximately 40% of rated load, the IGVs will continue to close (but never less than approximately 42 DGA) and the unit will transfer out of Premix Steady State into Lean-Lean. And eventually as unloading continues it will transfer out of Lean-Lean and into Primary mode.
When IBH is enabled during a START, it will be active when the unit reaches FSNL (Full Speed-No Load; rated speed). It will remain active until the IGVs reach approximately 62 DGA as the unit is loaded, and the unit will transfer into Premix Steady State at approximately 40% of rated load. When IBH is enabled during a unit shutdown while operating in Premix Steady State IBH will become active as the IGVs approach approximately 62 DGA angle and the unit will remain in Premix Steady State until the load drops below approximately 40% of rated. IBH will continue to remain active until the unit drops below rated speed.
I don't know if this will serve your purpose. But it's all I got; all I can offer. (No I can't email it to you, or text it to you. You can copy the text and print it.)
If you have Mark V or newer turbine control system, you can trend the operation of IGV angles, IBH control valve position, load, and combustion mode, and produce a very nice graph which will depict all of this very nicely. No words, but actionable data--and for your specific machine. For Mark V, the function is called Short Term Trending. For Mark VI and Mark VIe the function is called Trend Recorder or Trender.
Hope this helps! ('Please' and 'thank you' are good words to use when asking for help/information/assistance using the English language.... 'Doubt' IS NOT a good word to use when asking for help or clarification when using the English language.)
Finally, there is a 'Search' feature at the top of every Control.com webpage. It can be used to search all past posts and responses on Control.com. Every past post and response(s) are available using the 'Search' feature. And, this topic (IBH operation) has been covered MANY times before on Control.com.
J | IBH (inlet bleed heat) has lost its marbles | Power Generation | 6 | |
T | 7 FA Inlet Bleed heating | Power Generation | 3 | |
V | inlet bleed heat control | Power Generation | 3 | |
F | Inlet bleed heating control | Power Generation | 1 | |
A | Inlet Bleed Heating | General Automation Chat | 1 |