Hi there,
I'm having difficulty in an instrumentation system that I’ve installed on a trailer. What this trailer does is it basically heats up a bunch of tar and then pumps it into cracks on the ground.
The instrumentation consists of the following
4 Hobo Data Loggers
4 PD-785 Temp Displays
3 Type K Thermocouples
-1 For Measuring the Heating Oil Temperature (Oil that surrounds the tar is heated by a diesel burner that in turn heats the tar tank)
-1 For Measuring the Tar Temperature
-1 For Measuring the Pump Temperature (The temperature of the tar as it is pumped into the crack).
1 RTD (Ambient Temp Sensor)
All thermocouples are wired properly with Type K thermocouple wire.
The Precision Digital Displays are wired to a common ground (the display housing box which is then wired to the frame of the trailer) and are powered from a common power line running from the ignition switch on the trailer that starts the burner (each meter is wired with a separate 5amp fuse coming off this main line).
The problem is that after first installing these probes on the unit and firing the unit up and letting it get up to temperature, the temperature for the Tar is approximately 50'C below what it should be (We used two different bi-metal gauges and they both measured around 150ish 'C while the thermocouple read 100'C)
As well, the heating oil temperature read about 110'C which is also impossible, as the heating oil temperature is always above what the tar temperature is (in this case it is 150'C)
We were unable to test the pump temperature as the pump failed on the unit during testing.
I got a separate supply of type K extension wire and re-wired up the tar tank to see if perhaps it was a bad shipment of wire, and unfortunately that is not the case (the reading stayed the same). So now the only two possibilities that I can think of are a damaged thermocouple giving incorrect readings, or the precision digital displays are not calibrated correctly (According to the manufacturer they are pre-calibrated at the manufacturing plant though).
As this is the first instrumentation setup I’ve worked on I'm not really sure what to do. I've been searching google for some information on this problem, and another possibility seems to be a ground loop error. Would this be possible?
Any input would be much appreciated.
Thank you for your time,
Michael Cowie
I'm having difficulty in an instrumentation system that I’ve installed on a trailer. What this trailer does is it basically heats up a bunch of tar and then pumps it into cracks on the ground.
The instrumentation consists of the following
4 Hobo Data Loggers
4 PD-785 Temp Displays
3 Type K Thermocouples
-1 For Measuring the Heating Oil Temperature (Oil that surrounds the tar is heated by a diesel burner that in turn heats the tar tank)
-1 For Measuring the Tar Temperature
-1 For Measuring the Pump Temperature (The temperature of the tar as it is pumped into the crack).
1 RTD (Ambient Temp Sensor)
All thermocouples are wired properly with Type K thermocouple wire.
The Precision Digital Displays are wired to a common ground (the display housing box which is then wired to the frame of the trailer) and are powered from a common power line running from the ignition switch on the trailer that starts the burner (each meter is wired with a separate 5amp fuse coming off this main line).
The problem is that after first installing these probes on the unit and firing the unit up and letting it get up to temperature, the temperature for the Tar is approximately 50'C below what it should be (We used two different bi-metal gauges and they both measured around 150ish 'C while the thermocouple read 100'C)
As well, the heating oil temperature read about 110'C which is also impossible, as the heating oil temperature is always above what the tar temperature is (in this case it is 150'C)
We were unable to test the pump temperature as the pump failed on the unit during testing.
I got a separate supply of type K extension wire and re-wired up the tar tank to see if perhaps it was a bad shipment of wire, and unfortunately that is not the case (the reading stayed the same). So now the only two possibilities that I can think of are a damaged thermocouple giving incorrect readings, or the precision digital displays are not calibrated correctly (According to the manufacturer they are pre-calibrated at the manufacturing plant though).
As this is the first instrumentation setup I’ve worked on I'm not really sure what to do. I've been searching google for some information on this problem, and another possibility seems to be a ground loop error. Would this be possible?
Any input would be much appreciated.