Hey folks,
Hope you are all doing well!
We have a old BRUSH Electric Motor-Generator Set at our site. Recently during servicing, we noticed that the insulation on the Rotor poles was removed/eroding at places(See attached picture). Bare copper can be seen being exposed.
This was concerning but the machine has been running well since past 29 years without any problem and all electrical tests i.e. IR and PI are Okay.
I asked BRUSH rep. about it and he said this happens with old machines and should not pose any imminent threat. I disagree with his statement as I fear an inter-turn short circuit can take place in such a situation if moisture ingress happens or some conductive dusts accumulates over time. I intend to request management for complete rotor removal, dry-ice cleaning and re-varnishing urgently but since a lot of cost is involved I would like to be sure if the threat is real.
Please look at the picture and share your thoughts.
Regards,
Mutahir
Hope you are all doing well!
We have a old BRUSH Electric Motor-Generator Set at our site. Recently during servicing, we noticed that the insulation on the Rotor poles was removed/eroding at places(See attached picture). Bare copper can be seen being exposed.
This was concerning but the machine has been running well since past 29 years without any problem and all electrical tests i.e. IR and PI are Okay.
I asked BRUSH rep. about it and he said this happens with old machines and should not pose any imminent threat. I disagree with his statement as I fear an inter-turn short circuit can take place in such a situation if moisture ingress happens or some conductive dusts accumulates over time. I intend to request management for complete rotor removal, dry-ice cleaning and re-varnishing urgently but since a lot of cost is involved I would like to be sure if the threat is real.
Please look at the picture and share your thoughts.
Regards,
Mutahir