Insulation Resistance of oil filled transformer

P

Thread Starter

panthripu

We recently performed IR test on our oil filled transformer on the primary winding with 5000V tester. At first moment I was surprised to see the value, almost around 200MOhm as The rated voltage of primary is 34.5kV. When I checked the original test values during commissioning, it was 250MOhms. This transformer is in service now. But I still think that all the thumb rules and formulas meant to know the IR value are not at all useful. Sometimes it may create a big confusion if the original values are not known.

Comments????
 
Top