Dear All,
I have De Dietrichthermique Boiler control system that I'm trying to integrate with Satchwell Sigma IC-Modbus. The problem here that IC-Modbus is master RTU device, but the De Dietrichthermique boiler control system accesses the bus 5 seconds as master RTU and 5 seconds as slave RTU.
When I have spied on the bus to analize the protocol I found that the demand and response messages not standard.
1 Rx: \021\003\000\101\000\005\150\194\000\000\000
Above you can find that there is extra two bytes at the end of the message, where IC-LON cannot process.
I suppose here that I need a device to take control of data conversion and bus monitoring at one side, while to be slave RTU on the other side to connect with IC-Modbus.
Please advise me how to solve this problem, if you know such device.
Best Regards,
Jibreel Abdeen