Load Cell signal Cable
Arun Meyyappan
Can i use a 1.0Sq. mm signal cable to transmit a load cell output signal from the field to control room at an opproximate distance of 200 mtrs" what are the possible defects that can occurs on the receiving end.
Can i get specfication for the Load cell cable?
For a typical cell your cable should be shielded with 6 wires (3 pair)
Pair 1 from the control room to power the cell (excitation)
Pair 2 to bring back the cell output
Pair 3 to read back the cell excitation voltage. Pair 3 is normally connected to the same cell terminals as pair 1 and reads the actual voltage applied across the cell. As you know the cell output is rated in mV/V so it's important to ignore the voltage drop in pair 1
I have often used twisted pair instrument cable for this purpose however a 6 conductor shielded will also work.
If your cell is not used for a weigh scale and accuracy is not required you may get away with just 4 conductor shielded.
Post your systems Make & Model, you might get a clearer answer. Most system manuals show how to extend the cell cables
Good luck
Roy
as u said i am using a 3 pair, 6 core shielded cable for the millivolt transmission. Can u pls specify what is the max distance signal will not be effected? pls help.