Magelis xbt-p011010

W

Thread Starter

wissam

please help
i have a mchine which uses pl7 micro and magelis xbt-p011010, the problem happened when the error lamp on the pl7 micro is on.

i have the orginal application and i transfer it to the plc. the plc run just fine (green led is on) but when i tried to control the machine as normal using xbt-p011010, nothing happen except error messge appear on xbt screen and the error message is (dialog table authoriza incorect).

What is the meaning of this error? is ther still a problem in the plc or the problem in the xbt pannel. i have also the original xbt application if i transfer it to the xbt pannel would this solve the problem?
 
There is an authorisation word set in the plc.

you need to check what the word should be in the magelis software in the configuration menu and correct it.

There must have been some alteration to the program either on the plc or xbt to have caused this

the trouble is if buttons have been configured to certain bit for example they need to match on both the plc and xbt - this is the reason for the authorisation word.

if the old programs are from the same date they may both work if loaded together but you may lose some modifications.
 
Top