Gas turbine was operating at 23MW load. Suddenly following sequence of alarms appeared and turbine got tripped.
17.03.36.125 1 Q 0062 ALM COMMON IO COMMUNICATION LOSS
17.03.36.125 1 Q 0079 ALM LUBE OIL TANK TEMPERATURE LOW
17.03.36.187 1 L43FG EVT GAS FUEL SELECTED
17.03.36.218 1 Q 0120 ALM EXHASUT TEMP HIGH
17.03.36.218 1 Q 0121 ALM EXHAUST OVER TEMP TRIP
17.03.36.218 1 Q 0391 ALM COOLING WATER TANK LOW
17.03.36.218 1 Q 0392 ALM COOLING WATER TANK LOW LOW
17.03.36.250 1 L83CAPCAN EVT LOAD SELECTION CANCEL LOGIC
17.03.36.312 1 L4T EVT MASTER PROTECTIVE / TURBINE TRIP
17.03.43.750 0 Q 0062 ALM COMMON IO COMMUNICATION LOSS
I tried to find out alarm generation cause for "Communication loss" from Mark V manuals but could not find it. Can you please help to identify the cause of this alarm and why it should trip gas turbine on exhaust temp trip? Exhaust temperature trends were showing no abnormality. Also there are two HMIs connected to Mark V system through C and D core. Data loss was on HMIs was reported for few seconds at the time of trip.
17.03.36.125 1 Q 0062 ALM COMMON IO COMMUNICATION LOSS
17.03.36.125 1 Q 0079 ALM LUBE OIL TANK TEMPERATURE LOW
17.03.36.187 1 L43FG EVT GAS FUEL SELECTED
17.03.36.218 1 Q 0120 ALM EXHASUT TEMP HIGH
17.03.36.218 1 Q 0121 ALM EXHAUST OVER TEMP TRIP
17.03.36.218 1 Q 0391 ALM COOLING WATER TANK LOW
17.03.36.218 1 Q 0392 ALM COOLING WATER TANK LOW LOW
17.03.36.250 1 L83CAPCAN EVT LOAD SELECTION CANCEL LOGIC
17.03.36.312 1 L4T EVT MASTER PROTECTIVE / TURBINE TRIP
17.03.43.750 0 Q 0062 ALM COMMON IO COMMUNICATION LOSS
I tried to find out alarm generation cause for "Communication loss" from Mark V manuals but could not find it. Can you please help to identify the cause of this alarm and why it should trip gas turbine on exhaust temp trip? Exhaust temperature trends were showing no abnormality. Also there are two HMIs connected to Mark V system through C and D core. Data loss was on HMIs was reported for few seconds at the time of trip.