We are tuning to governors on our large Island system and we have a couple units with Mk V controllers. One set is on two 66MW steam turbines (Mk V triple redundant, EX2000, EHC, WinNT HMI). Other one is on a frame 5 40MW gas turbine running liquid fuel (diesel) ONLY and an iDos.
I'm familiar with the system and organization of constants, etc. I've viewed the constant txt file. However, I am having trouble finding which constants control the characteristics of the governor in various modes like speed, isoc, base. We have a GE TA coming to help tune, but I'd like to get these values ahead of time to analyze.
I would like to know the following and any other applicable constants used: droop %, ramp rate, time constants, gain, mode change limits, etc. The steam units are very slow to increase load when running in droop. However, they reject load pretty fast (I can view trends using historian).
Secondly, on the gas turbine unit, the testing company wants to record fuel valve position. On the steam units he just places a temporary LVDT on the actuators--obviously this doesn't work on the liquid fuel valve. He doesn't have a LVDT signal conditioner so he can't "piggy back" on the position signal from the fuel valve.
Is it possible in MarkV Idos to create an analog output (voltage or current) of the fuel valve position? There are plenty of spare I/O's on the cards.
Thanks in advance.
I'm familiar with the system and organization of constants, etc. I've viewed the constant txt file. However, I am having trouble finding which constants control the characteristics of the governor in various modes like speed, isoc, base. We have a GE TA coming to help tune, but I'd like to get these values ahead of time to analyze.
I would like to know the following and any other applicable constants used: droop %, ramp rate, time constants, gain, mode change limits, etc. The steam units are very slow to increase load when running in droop. However, they reject load pretty fast (I can view trends using historian).
Secondly, on the gas turbine unit, the testing company wants to record fuel valve position. On the steam units he just places a temporary LVDT on the actuators--obviously this doesn't work on the liquid fuel valve. He doesn't have a LVDT signal conditioner so he can't "piggy back" on the position signal from the fuel valve.
Is it possible in MarkV Idos to create an analog output (voltage or current) of the fuel valve position? There are plenty of spare I/O's on the cards.
Thanks in advance.