We had to replace SDCC and TCPS cards in <R> core. R core power supply switched off in <PD> and subsequently the TCPS card was replaced. When we disconnect the JP1 connector in TCPS card the following alarms are generated and drives were getting on and off:
<S> 0047 DCC I/O card Obj ID#4 reset (diagnostic alarm)
Emergency LO pump running
Fire in Zone#1, 2, 3
Manual trip local & remote
Normal shutdown protective lock out
Customer trip
Hydraulic protective trouble
MCC under voltage
We suspended the work as the machine was on turning gear and turning operation was getting interrupted.
We have done the same exercise after stopping the turning gear. This time we found that TCD1 card was rebooting (changing A2 to A7 state continuously) when JP1 connector is disconnected in <R> computer TCPS card.
Each core is equipped with TCPS card and it supplies the required voltages to cards in that core. Something is wrong in our system. Anybody has this kind of experience? Please share with me.
Regards,
ankarao
<S> 0047 DCC I/O card Obj ID#4 reset (diagnostic alarm)
Emergency LO pump running
Fire in Zone#1, 2, 3
Manual trip local & remote
Normal shutdown protective lock out
Customer trip
Hydraulic protective trouble
MCC under voltage
We suspended the work as the machine was on turning gear and turning operation was getting interrupted.
We have done the same exercise after stopping the turning gear. This time we found that TCD1 card was rebooting (changing A2 to A7 state continuously) when JP1 connector is disconnected in <R> computer TCPS card.
Each core is equipped with TCPS card and it supplies the required voltages to cards in that core. Something is wrong in our system. Anybody has this kind of experience? Please share with me.