Dear all,
I want to investigate a curious finding that happened at our site few days back.
We have a PLC Rack which is supplied through a standard 2 Pole, 2A, Schneider Electric IC60N MCB. The breaker tripped and the PLC shutdown which impacted a critical process.
When we were checking why the breaker tripped, we couldn't find any fault. However, we noticed that when we turned on the breaker and monitored the amps drawn through a meter, the current was 2.4A(The breaker is rated at 2A). We checked the load after various intervals and it was 2.4A consistently.
The breaker had been installed 5 years back and we think since then it has been running at 2.4A and not tripped. We did an experiment where we installed an identical new IC60N breaker and this one, with equal load and noticed behavior. Both kept on running on 2.4A for 5 hours. When we applied heat on them through a temperature gun, the old breaker tripped, while the new one remained on.
It is also worth noting that the breaker is AC whereas the circuit it is installed is on 24VDC.
I want to know why a breaker which was running on 2.4A since 5 years suddenly trip now? What things I should investigate more?
Looking forward to your insights.
Regards,
Mutahir
I want to investigate a curious finding that happened at our site few days back.
We have a PLC Rack which is supplied through a standard 2 Pole, 2A, Schneider Electric IC60N MCB. The breaker tripped and the PLC shutdown which impacted a critical process.
When we were checking why the breaker tripped, we couldn't find any fault. However, we noticed that when we turned on the breaker and monitored the amps drawn through a meter, the current was 2.4A(The breaker is rated at 2A). We checked the load after various intervals and it was 2.4A consistently.
The breaker had been installed 5 years back and we think since then it has been running at 2.4A and not tripped. We did an experiment where we installed an identical new IC60N breaker and this one, with equal load and noticed behavior. Both kept on running on 2.4A for 5 hours. When we applied heat on them through a temperature gun, the old breaker tripped, while the new one remained on.
It is also worth noting that the breaker is AC whereas the circuit it is installed is on 24VDC.
I want to know why a breaker which was running on 2.4A since 5 years suddenly trip now? What things I should investigate more?
Looking forward to your insights.
Regards,
Mutahir