Measuring Low Flow than Actual

Q

Thread Starter

Qasim Maqbool

I am Facing Low Flow measuring Problem in Electromagnetic Flowmeter Siemens SITRANS F M MAGFLO Model MAG 6000.

I Tried all Troubleshooting Problem as mentioned in its vendor Manual.
I have also try to change it excitation frequency but unable to get result. I also switched off its Power supply for 15 minutes and again ON. But it is still in his own MOde, Showing low measuring Value.

Kindly give me Suggetion.

[email protected]
 
J

Jason Semple

How old is the meter and where are you located? Siemens have a Field Checklist which steps you through the field checks to help diagnose any potential problems with the flow meter.

I could email you the checklist if you like.

Jason
 
A few particulars to check:

- Check that the units of measure are set correctly.

- Confirm that the pipe is full.

- Compare the displayed flow with actual. Is it off by a constant factor?

- Look at both flow rate and total - are both off?
 
R
One problem I have seen in mag flow meter was one of the elsctrode seals leaking causing a low resistance to ground. This effectively cuts the voltage in half with a corresponding drop in signal output.

Just empty the tube, disconnect electrodes and check resistance.

Roy
 
D

Dave Scarlett

Siemens has a "Varificator" that can fully check the condition of their flow meter on line. I suggest you contact your local rep.
 