Melsec AJ71PB92 profibus parameter set

R

Thread Starter

Romeli

Dear any one,

We had difficulties to set-up parameter for new plc card AJ71PB92D, this is a new card type to replace AJ71PB92. Our local vendors (Singapore & Jakarta) just only give us GX configurator sofware v.6.0. But cannot up-load from original card. Whats kind parameter must be set-up at new PLC card. What kind software needed, Why Mitsubishi vendors cannot solve this problem? Please any one can help me, how to set-up new card.

thanks,

--
Romeli
Electrical engineer
PT.Smelting
Affiliate of Mitsubishi Materials
phone: 62-31-3976464 fax: 62-31-3976466
www.smelting.co.id
 
F

Frank de Jong

If you want to upload the original configuration, you need the software profimap v1.00. For the GX configurator you need the slaves GSD files. If there are only Mitsubishi slaves the are allready included in the software.

Give the master a FDL adres, leave other configuration parameters at default. Choose the master you needed, 0-Mode or E-mode (how many bytes you need to transfer between master and slaves, 0-Mode is 32 bytes send and 32 bytes receive for every slave, E-Mode set per slave the amount of bytes(directly imported from GSD files)). Configure your network. Write the configuration file in the PB92D module, through the CPU. Finally create pou and import the pou (ASC file) in the GX-IEC Developer software.
In the PLC programming software a sub program (POU) is automatically created, witch will startup the profibus network and refresh the slaves information by from/to instructions.

kindly regards
Frank de Jong
Getronics
Netherlands
 