Dear All
There is a very curious case that occurred at our site against which I am sharing details. Will appreciate if others can pitch in if they have had similar experiences.
We have a few IC60N 2A C Type MCB breakers (manufactured by Schneider Electric) installed at a critical PLC panel installed at our site. Recently we faced an issue of tripping of one of these breakers. During investigation it was observed that 2.4 Amps were flowing through the breaker however what was concerning was that breaker has been in service for the past 4 years approximately without tripping since. We have checked and load has been constant throughout. We have the following 3 queries for which we need support from this forum members.
1. What is the tolerance margin available for these breakers
2. Can voltage rating of application affect the operation of these breakers? Breaker is rated for 440VAC whereas it had been installed on a 24VDC circuit.
3. Do these breakers have ambient temperature compensation in them? We carried out thermography after taking load back in service and maximum observed temperature rise on the breaker was found to be 38 degrees Celsius. On the breaker datasheet it states that the reference temperature of the breaker tripping curve is 50 degrees Celsius. Is it possible that due to low ambient around the breaker, the heat generated by the flowing current was less to prevent the bi-metallic element initiate tripping of the breaker?
4. Is it possible that due to continuous operation near the rated condition the Bi-metallic strip has faced wear and tear overtime and ultimately resulted in nuisance tripping.
We carried out bench test of a new breaker of similar rating and this breaker and the results of bench test are also attached with this post. Can anyone shed some light on the above queries.
There is a very curious case that occurred at our site against which I am sharing details. Will appreciate if others can pitch in if they have had similar experiences.
We have a few IC60N 2A C Type MCB breakers (manufactured by Schneider Electric) installed at a critical PLC panel installed at our site. Recently we faced an issue of tripping of one of these breakers. During investigation it was observed that 2.4 Amps were flowing through the breaker however what was concerning was that breaker has been in service for the past 4 years approximately without tripping since. We have checked and load has been constant throughout. We have the following 3 queries for which we need support from this forum members.
1. What is the tolerance margin available for these breakers
2. Can voltage rating of application affect the operation of these breakers? Breaker is rated for 440VAC whereas it had been installed on a 24VDC circuit.
3. Do these breakers have ambient temperature compensation in them? We carried out thermography after taking load back in service and maximum observed temperature rise on the breaker was found to be 38 degrees Celsius. On the breaker datasheet it states that the reference temperature of the breaker tripping curve is 50 degrees Celsius. Is it possible that due to low ambient around the breaker, the heat generated by the flowing current was less to prevent the bi-metallic element initiate tripping of the breaker?
4. Is it possible that due to continuous operation near the rated condition the Bi-metallic strip has faced wear and tear overtime and ultimately resulted in nuisance tripping.
We carried out bench test of a new breaker of similar rating and this breaker and the results of bench test are also attached with this post. Can anyone shed some light on the above queries.
Attachments
-
130.8 KB Views: 17
-
151.7 KB Views: 10