I have read through all I can find and have reviewed the CSP generated by the MKV (TTXMV4 and TTXSPV4). Checked all the control constants associated with the generation of the exhaust thermocouple arrays, average calculations, spread calculations and spread limit calculations. A frame 6 unit suffered an instantaneous single exhaust thermocouple fail high event which resulted in the three spreads being exceeded and a trip occurring. All control processors were healthy, all other exhaust thermocouples were healthy and within a 15F degrees of each other. The rogue thermocouple stepped up to 2046F in 3 seconds, stayed there till the unit tripped then returned to a value similar to the other T/C. Adjacent T/C were stable. The unit operation was stable, flame detection count remained unchanged during the event, as did load. I conclude that the temperature being sensed by this single T/C was false.
I appreciate that the dominant fail mode for thermocouples connected to a MKV is to fail low, but when there is a fail high event this single sensor failure appears predictably to trip the unit. I have convinced myself that this scenario is correct and is part of the GE design, however I would appreciate a sanity check if there are any other views out there. I appreciate that the average is calculated differently with a low threshold acceptance and discarding highest and lowest so it is much more immune to T/C failures. Not so the combustion monitor.
I appreciate that the dominant fail mode for thermocouples connected to a MKV is to fail low, but when there is a fail high event this single sensor failure appears predictably to trip the unit. I have convinced myself that this scenario is correct and is part of the GE design, however I would appreciate a sanity check if there are any other views out there. I appreciate that the average is calculated differently with a low threshold acceptance and discarding highest and lowest so it is much more immune to T/C failures. Not so the combustion monitor.