We are using Schneider Electric's 174-CEV-300-10 Ethernet Bridge on a Modbus RTU protocol RS485 2-wire bus to communicate with 13 DMMS 300+ Power Meters. The meters respond one at a time and polling is not possible for more than 1 meter at a time.
Main protocol is ModbusTCP and the Ethernet converter, being master, communicates with slave devices (power meters). Modbus runs on standard 2-wire RS485, connecting all 13 power meters. Each power meter is configured with unique ID no. Each Meter data communicates independently when polled, but any 2 meters fail to communicate or poll the data together. Anyone knows the solution? If any configuration should be changed for the Ethernet converter?
Main protocol is ModbusTCP and the Ethernet converter, being master, communicates with slave devices (power meters). Modbus runs on standard 2-wire RS485, connecting all 13 power meters. Each power meter is configured with unique ID no. Each Meter data communicates independently when polled, but any 2 meters fail to communicate or poll the data together. Anyone knows the solution? If any configuration should be changed for the Ethernet converter?