Modbus RTU Passive Taps

S

Thread Starter

Shawn H

I am designing a 300m two wire Modbus RTU network with a PLC master. I will try to daisy chain my slave devices (29 devices) but require several taps off my trunk line. How long can these taps be? I have read information saying they must be less than 1m and I have also read that the taps cannot be more than 20m in length. Please confirm.

Also..does having passive taps reduce the overall trunk length?

Thanks
Shawn
 
RS485 2 wire 1/2 duplex cannot have any "Tap length". There are only 2 ends to an RS485 highway.
 
J
If baud rate is below 19200 and bus lenght below 100 meters, there will be no problem with your topology. Problems arise when both (or any) of baud rate and/or bus length increases.
 