Modbus RTU Serial Master & Slave

D

Thread Starter

Darryl Hayes

I have two electrical meters that are communicating to two external users (via DNP3). Each user requires data from both meters. I have two serial ports on each meter.

One of the serial ports on each meter is used for the external communications. I can connect the two meters together on the second port. I can make this work one-way by setting one meter as the master and the second as a slave. How can I get data from the first meter to the second at the same time.
 
R

R. van der Tas

Modbus master is able to read data (e.g. obtain from Dev1 into Dev2) and write data (send data from Dev2 into Dev1). Since this is bi-directional, one serial connection should be sufficient to provide the bi-directional comms.

An alternative would be that you install a Modbus Master OPC Server on the computer and an OPC bridge software component (e.g. DataWorX32). You can download it from
http://www.iconics.com/support/free_demos.asp
Now the bridge software will communicate the changes in values between the two (or more) devices.

regards
Raymond van der Tas
 