Modbus to Backnet

A

Thread Starter

Anonymous

I'm involved in a project where the HVAC control company wants to use a BACnet based control system. We are installing a Crestron control system and would like to use the Crestron approved Modbus modules to communicate with the BACnet based system. I was informed that there is a Modbus to BACnet data converter that allows the two protocols to communicate and share data.
I have been unable to find such a device. Help!
 
The fieldserver product is a good answer... I have used the Allen-Bradley DF-1 to BACnet flavor and it worked great. The setup was some what tricky, but Tech. support was helpful.
 
J

Jim MacKinnon

Check out Tridium.com

We provide an extensive software framework that talks LON and BacNet "out of the box", and have (amongst many others) a driver for ModBus.

Pls contact me if you want further info: [email protected]
 
Y

Yogesh Deshmukh

Aftek's Modbus to BACnet converter (APC-BM series) is used to integrate HVAC systems (VAV boxes, VRF ACs, chillers) with Building management systems.

For further details visit http://apc.aftek.com .

You can send your inquires at apc [at] aftek.com
 
Top