I would like to know if anyone has any experience with the Modicon Momentum High Speed Counter Module (170 AEC 920). I'm have a bit of trouble with one. My incoming signal is from a Faure
Herman turbine meter and preamp. The magnetic pick-up in the meter sends a mV signal to the preamp where it is shaped and put on the wire by pulsing the current between 3mA and 44mA. At the counter module a 1 watt 270 ohm resistor was put across the input as directed by Faure Herman to give us a voltage pulse instead of a current pulse. Using a oscilloscope I discovered
that the square wave was not from 1VDC to 11VDC as would be expected at 24 VDC, but from 9.7VDC to 22VDC. I increased the resistor at the input until my square wave was from 3VDC to 22VDC. According to the spec, the module sees logical state "1" at 11VDC or higher and logical state "0" at 5VDC or lower. So my square wave should fall well within the spec. However, when
the frequency is measured at the magnetic pick-up and after the pre-amp, the frequency is the same, but the frequency I calculate from the counter
register in the PLC is higher. As I initially increased the resistor value at the input module, the calculated frequency got closer and closer to the input frequency. But at 1.8 KOhms, the PLC started giving wild readings. Right now the resistor is at 1.5 KOhms and my square wave is at the above mentioned levels 3VDC for the low and 22VDC for the high, and I'm about 1Hz higher in the PLC than the frequency measured at the input. However, if I use a pulse generator, to input a signal to the PLC, the frequency in the
PLC matches that produced by the generator. But the pulse generator produces a square wave from 0VDC to 16VDC.
If anyone could shed some light on this problem, I would greatly appreciate it.
Thanks,
Brady Matherne
PLC / SCADA Tech
Panel Specialists, Inc.
[email protected]
Herman turbine meter and preamp. The magnetic pick-up in the meter sends a mV signal to the preamp where it is shaped and put on the wire by pulsing the current between 3mA and 44mA. At the counter module a 1 watt 270 ohm resistor was put across the input as directed by Faure Herman to give us a voltage pulse instead of a current pulse. Using a oscilloscope I discovered
that the square wave was not from 1VDC to 11VDC as would be expected at 24 VDC, but from 9.7VDC to 22VDC. I increased the resistor at the input until my square wave was from 3VDC to 22VDC. According to the spec, the module sees logical state "1" at 11VDC or higher and logical state "0" at 5VDC or lower. So my square wave should fall well within the spec. However, when
the frequency is measured at the magnetic pick-up and after the pre-amp, the frequency is the same, but the frequency I calculate from the counter
register in the PLC is higher. As I initially increased the resistor value at the input module, the calculated frequency got closer and closer to the input frequency. But at 1.8 KOhms, the PLC started giving wild readings. Right now the resistor is at 1.5 KOhms and my square wave is at the above mentioned levels 3VDC for the low and 22VDC for the high, and I'm about 1Hz higher in the PLC than the frequency measured at the input. However, if I use a pulse generator, to input a signal to the PLC, the frequency in the
PLC matches that produced by the generator. But the pulse generator produces a square wave from 0VDC to 16VDC.
If anyone could shed some light on this problem, I would greatly appreciate it.
Thanks,
Brady Matherne