Modicon RTD Module 140 ARI 030 10

M

Thread Starter

MIKE ROCHE

I Am trying to read negative temperatures (-200 F). I can't get the module to read negative numbers. Module reports values in Engineering units but negative values don't display properly. Why? What do I have to do read negative values? correctly
 
Set the format to INT format. This will use negative values. (See Online> RDE online) May be your input is configured for UINT, which is unsigned Integer format...
 
Top