We have two 80MW Steam Turbines of Alstom make. We want to perform a modification that if one ESV closes during normal operation, our Steam turbine keep running with one ESV.
We actually have been facing problems on one of the steam units that it has tripped several times because one of its ESV solenoid's coil burn due to which ESV closes and cosequently turbine trips. When coil of solenid burns and because of which one ESV closes then indication "Stem turbine set to reset" appears and m/c trips with in 5 seconds.
We now want to make a modification to increase T/B trip time up to 30 seconds so that whenever above said indication appears operator on duty has enough time to open T/B bypass valve manually and hence tripping may be avoided.
Now what we are afraid of about this modification is that 30 seconds delay time in tripping without bypass open may cause over pressue in system which may lead to some extensive damage.
Please advise
[email protected]
We actually have been facing problems on one of the steam units that it has tripped several times because one of its ESV solenoid's coil burn due to which ESV closes and cosequently turbine trips. When coil of solenid burns and because of which one ESV closes then indication "Stem turbine set to reset" appears and m/c trips with in 5 seconds.
We now want to make a modification to increase T/B trip time up to 30 seconds so that whenever above said indication appears operator on duty has enough time to open T/B bypass valve manually and hence tripping may be avoided.
Now what we are afraid of about this modification is that 30 seconds delay time in tripping without bypass open may cause over pressue in system which may lead to some extensive damage.
Please advise
[email protected]