Hey Folks,
Just curious if anyone has experienced problems arising from moisture in the CPD pressure transmitter sensing lines.
We recently experienced a trip when two of the three CPD sensors stopped tracking and slowly trended upwards until we reached the trip point. The unit is a frame 7AE. The consensus after the fact was that 2 of the 3 lines froze off (ambient temps were low in the building that day).
After restarting the unit we gently blew down the sensing lines while the unit was in operation and found a bit of water in the dead legs.
Do any of you blow down these transmitters regularly? And is there an issue taking them out of service one at a time while on the run? My understanding is that the MarkVIe selects the median CPD reading as the control variable, so isolating one temporarily shouldn't cause an issue, but we weren't brave enough to try.
Thanks!
Just curious if anyone has experienced problems arising from moisture in the CPD pressure transmitter sensing lines.
We recently experienced a trip when two of the three CPD sensors stopped tracking and slowly trended upwards until we reached the trip point. The unit is a frame 7AE. The consensus after the fact was that 2 of the 3 lines froze off (ambient temps were low in the building that day).
After restarting the unit we gently blew down the sensing lines while the unit was in operation and found a bit of water in the dead legs.
Do any of you blow down these transmitters regularly? And is there an issue taking them out of service one at a time while on the run? My understanding is that the MarkVIe selects the median CPD reading as the control variable, so isolating one temporarily shouldn't cause an issue, but we weren't brave enough to try.