NEC:
Can anyone direct me to the appropriate sections of the NEC which defines class II wiring methods?
IEC:
Where can I find type II coordination rules and tables?
thnx
john
T
John,
NEC Code for Class II Locations is covered in Article 502. Wiring methods are covered in 502-4 (a) and (b).
Do not have refs from IEC.
Hope this helps,
Tony
Tony Firth, Elect.Eng.,
Quester Technology Inc.
Fremont, CA 94539
W
William L. Mostia, Jr
In regards to Class II wiring and the NEC, Article 725 is the article you want.
Also, there is an article, "Classification of circuits under Article 725," in the September 1998 of CEE News by Noel Williams. This is the only article that discusses instrument level wiring that I have seen on this subject. It can
be found at: http://www.ceenews.com/archive/809ce19.htm
William(Bill) L. Mostia, Jr. PE
Principal Engineer
WLM Engineering Co
Independent I&E Consultant
P.O. Box 1129
Kemah, TX 77565 USA
E-Mail: [email protected]m
These opinions are my own and are offered on the basis of Caveat Emptor.