A system (filtration system) developed in Germany with a control panel designed in Germany to me CE requirements may be sold here in the US. I have reviewed the drawings from Germany and am not sure if it meets NEC requirements. The one big issue I see so far is as follows:
The disconnect (480V 3 phase power supply required) is on the door and is not interlocked such that the door can be opened without power being removed. This is a requirement of NFPA 79, but I don't see it in the NEC (NFPA 70), though the NEC refers to NFPA 79. There is a question as to whether the filtration system is an industrial machine, so NFPA 79 may not apply by itself.
The only other thing I see is there will need to be added markings per articles 409.110 and 670.3.
Opinions?
The disconnect (480V 3 phase power supply required) is on the door and is not interlocked such that the door can be opened without power being removed. This is a requirement of NFPA 79, but I don't see it in the NEC (NFPA 70), though the NEC refers to NFPA 79. There is a question as to whether the filtration system is an industrial machine, so NFPA 79 may not apply by itself.