i have a device which works on RS 422 four wire , but does not have any identity of its own ( means there is no option for putting any address ). i need to connect 88 devices on a single system, how can i do this ?
Oem/vendor type model of the devices...i have a device which works on RS 422 four wire , but does not have any identity of its own ( means there is no option for putting any address ). i need to connect 88 devices on a single system, how can i do this ?
Original poster even gave a quick reply update... So bye byeWith RS-422 four wire you can only connect 2 devices to each other. So there is never a need to set an address - you always know whom you are talking to (= the other).
Now it could be that the vendor says "RS-422 four wire" but actually means: RS-485 four wire. In this case, the device being the master also doesn't need an address. Like in Modbus.
BTW, with RS-485 the normal max device limit per cable segment is 32. You need repeaters to reach 88.
by Seth Price