I'm a bit new to control and instrumentation, so I'm reading this book called <i>"Instrumentation for Process Measurement Control"</i>. The info is a bit out of date but where I'm working is a bit out of date so not a problem.
In a section explaining the operation of a <i>"Force-Balance Pneumatic Pressure Transmitter"</i>, specifically one based on a Bourdon tube for high pressure it says, "For safety, oil or liquid, never air, should be used for high pressure calibrations." The full paragraph is below.
I'm confused slightly why it would make any difference. I'm sure there is a good explanation, but initially I would see no difference between the two. If something breaks they'll both be at the same pressure I would have thought. I'm sure someone on this forum could explain it.
Book Excerpt
If the pressure to be measured is high, such as 5,000 psi or 35. MPa, a different sensing element is employed. The pressure being measured is applied to a Bourdon tube. This pressure tends to straighten the tube and causes a horizontal force to be applied to the lower end of the force bar. The diaphragm seat serves as both a fulcrum for the force bar and as a seal for the pressure chamber. The force is transmitted through a ftexure connector to the range rod, which pivots on the range adjustment wheel. Any movement of the rangerod causes a minute change in the clearance between the ftapper and nozzle. This produces a change in the output pressure from the relay to the feedback bellows until the force in the bellows balances the force created by the Bourdon tube. The output pressure, which establishes the force-balancing, is the transmitted pneumatic signal that is proportional to the pressure being measured. This signal is transmitted to a pneumatic receiver to record, indicate, or control. The calibration procedure for this transmitter is the same as for the low pressure transmitter, but the calibration pressure is developed with a dead weight tester. <b>For safety, oil or liquid, never air, should be used for high pressure calibrations.</b>
Book Excerpt