Open Circuit a Protection Current Transformer

C

Thread Starter

Chakrit

During initial loading of 6.6 kV Medium Voltage Switchgear we discovered that the main incoming circuit breaker protection current transformer (CT 2500:1 A) secondary circuits were open at 40A on primary current for 2 hrs and our EE engineer reconnect it with 40A still remain on primary (unsafe condition).

1. Dose this CT damage by abnormal high voltages ?

2. Whether this current transfomlers should be replaced or retested. If retesting, how to prove this CT still OK
 
P

Phil Corso, PE

Responding to Chakrit's Sep 23 query... it probably was not damaged having been subjected to only about twice its rated excitation ampere-turns!

However, testing requires three essential factors: sophisticated test equipment; skilled and knowledgeable test personnel; and great care. So, unless you possess or can obtain all three of the enumerated factors the CT should be replaced!

Regards,
Phil Corso, PE {Boca Raton, FL, USA}