Premium PLC Communication

R

Thread Starter

Rahul Patil

I'm having two Premium PLCs with ethernet module.
I want to communicate with both PLCs through ethernet.

How do I do it?
 
Communication via TCP is very simple when using the I/O scanner of the PLC's. Just fill in the slaves IP address, how often you want to read or write (Repeate Rate) and the slave registers location
 
READ_VAr, or WRITE_VAR if conditional. IO scanner if continous. Read Communications manual supplied with PL7 / Unity s/w.
 
R

Robert Willis

You have not mentioned what programming software or specific Ethernet modules or processors that you are using.

Depening on your specific hardware and software you can use the following:

1. Use the READ VAR and WRITE VAR EFB (All Controllers have this functionality)

2. Use the Ethernet I/O Scanner Function

3. Use the Gloabal Data FunctioN
 
A

aggattapauer

You may use I/O SCANNING. It's very easy to configure and it's not necessary to write any line of program (like read_var or send_req etc.)
 
Dear friend,

Thank you for your reply.
I'm using Premium PLC's TSX 573623 with PL7 Pro V4.4. 7 ATV71 drives also communicating with each PLC, i.e. PLC to PLC communication by using ethernet and PLC to DRIVE communication using CANopen.
 